Receptacle spacing
Q: The NECA Code Committee has reviewed a question regarding a large
single-family residence that has 25 ft. of permanent built-in bookcases
from floor to ceiling-whether or not that is usable wall space requiring
an outlet 6 ft. from the door in every 12 feet. I believe the question
being asked is: Does the receptacle spacing required by Article 210.52
apply to walls that have built in bookcases or similar locations?
A: Yes, the intent of Article 210.52(A)(2) of the 2002 NEC and E3801.1.1/210.52(A)(2)
of the One and Two Family Dwelling Code is quite clear. No point along
a wall space is to be greater than 6 ft. from a receptacle. The intent
for this section is to reduce the use of extension cords. In the case
of a bookshelf covering 25 ft of area, either receptacles installed in
the case, or floor receptacles installed within 18" of the case can
be used to meet the requirements.
(Tri-County Electrical Code Forum April 28, 2004)
|