Receptacles
1. Q. Is a receptacle within 36" from the edge of a bathroom basin acceptable even though it is below the edge? An example would be a pedestal basin in a powder room.
A. Yes. See 210.52(d)
2. Q. May someone install duplex receptacles in spaces dedicated for two appliances in a garage or basement , even if the appliances are not in place at final inspection? ?
A. Yes. The panel suggests marking the receptacle. (Tri-County Code Forum, November 7, 2002-Approved by the state code chief for statewide application) See 210.52(g), 210.8(A)(2)
3. Q. May a single receptacle for a dedicated space be installed for a new house when at final inspection the appliance is not in place and the house may still be for sale?
A. Yes, except for washing machines in bathrooms. (Tri-County Code Forum, November 7, 2002-Approved by the state code chief for statewide application)
4. Q. Dedicated furnace 20-amp 120-volt circuit: Can the condensate pump (furnace/ac) be tapped to the furnace circuit for single-outlet receptacles?
A. Yes, on 15-or 20-amp circuits. See Article 422.12, 2002 NEC. (January 23, 2003 Tri-County Code Forum; approved by state electrical code chief for statewide application)
|