Installation of Non-Metallic Boxes
1.Q. Art. 314-23(B)(1) States that nails (screws) used to fasten a box
shall be on the outside of the box or within ¼ of the back of the
box. Art. 370-43 states that attachment of nonmetallic box shall be on
the outside of the box or the box shall be so constructed so as to prevent
contact between the conductor and the supporting screws. Is it permissible
to install a nonmetallic box using screws at the front of the box and
installing a nonmetallic protection ring (stonco/goof ring) to prevent
contact between screws and conductors? Inspectors could note box location
on rough in and check box at final to make sure the ring is in.
A. Code does not allow this specific installation, but the code panel
could sympathize with specific circumstances in which such an application
would be acceptable. The code panel recommended that the contractor discuss
the installation in advance with an inspector and ask for an alternate
method if the need arises. (Tri-County Code Forum, May 9, 2002)
|